I'm having a little difficulty figuring out how to apply 220.43(A). I'm designing for a small retail space with a 100 Amp, 208Y/120V panel. There's one show window, which is about 6-1/2' wide. The owner does not plan to put any load in the show window, other than a light fixture across the top, but I've provided a duplex receptacle at the top of the window per 210.62. Since there's no specific load associated with that receptacle, I've assigned the branch circuit 180VA. So far, so good.
Here's where the confusion sets in. When calculating the feeder, 220.43(A) says I have to use 200VA/ft, rather than 180VA/duplex. Okay, I understand that. Since my window is 6-1/2' wide, I calculate 7' x 200VA = 1400VA. Now, do I apply that 1400VA to Phase B, since that's the phase that's feeding my show window receptacle, or do I split the 1400VA evenly between the three phases? This is my first time dealing with a show window, and I want to make sure I get it right.
Normally, I add up each of the three phases separately and then size the feeder based on the largest of the three. In this case, however, since the 1400VA is more of an allowance, rather than an actual load, I'm unsure how it should be handled.
Here's where the confusion sets in. When calculating the feeder, 220.43(A) says I have to use 200VA/ft, rather than 180VA/duplex. Okay, I understand that. Since my window is 6-1/2' wide, I calculate 7' x 200VA = 1400VA. Now, do I apply that 1400VA to Phase B, since that's the phase that's feeding my show window receptacle, or do I split the 1400VA evenly between the three phases? This is my first time dealing with a show window, and I want to make sure I get it right.
Normally, I add up each of the three phases separately and then size the feeder based on the largest of the three. In this case, however, since the 1400VA is more of an allowance, rather than an actual load, I'm unsure how it should be handled.