I look at 220.43 and it requires 200VA per foot for show windows branch circuit. Then 210.62 requires one receptacle for every 12 feet of window. If I have 12 feet of window that would be 2400va but this load would have to be considered continuous, so a 20 amp circuit wouldn't be adequate for receptacles spaced 12 feet apart. Then I looked at a Hollister remodel that I just bid. They show .720KVA with the required 2 receptacles one circuit for approximately 24 feet of show window on approved plans and the a PF Chang's with 24 feet of window and 600va on the panel schedule for load again one circuit 2 receptacles.