NEC 410.10(D) addresses lighting use in showers: essentially is must be "wet location".
I recall being called out at one time in the distant past on another standard that is evading all efforts to be found:
In addition to being "wet location", the fixture has to be "Approved For Use In Showers" (maybe a UL / NRTA standard?)
... any exposed metal on the room side of the fixture (ex; a metal overlap trim flange) has to be electrically isolated from ground (which could integral to the fixture's desicn and/or construction, or be achieved with no more than a manufacturer supplied foam gasket between the trim and the housing, provide the mounting clips did not 'connect' either.)
--> Is this a real thing, a thing of the past, or maybe no more than a flawed memory?
be well, stay healthy,
with many thanks in advance, m.
I recall being called out at one time in the distant past on another standard that is evading all efforts to be found:
In addition to being "wet location", the fixture has to be "Approved For Use In Showers" (maybe a UL / NRTA standard?)
... any exposed metal on the room side of the fixture (ex; a metal overlap trim flange) has to be electrically isolated from ground (which could integral to the fixture's desicn and/or construction, or be achieved with no more than a manufacturer supplied foam gasket between the trim and the housing, provide the mounting clips did not 'connect' either.)