I have always been of the mind that shower
lighting was recessed with wet listed
trims.....period. I have a wireman working for me that says
wall sconces are not prohibited per NEC 410.4.D
I read this several times
and it DOES not specifically exclude wall
sconces. If wet-listed fixtures are used, have I been wrong all these years?
Jim
lighting was recessed with wet listed
trims.....period. I have a wireman working for me that says
wall sconces are not prohibited per NEC 410.4.D
Code:
(D) Bathtub and Shower Areas. No parts of cord-connected
luminaires (fixtures), hanging luminaires (fixtures),
lighting track, pendants, or ceiling-suspended (paddle) fans
shall be located within a zone measured 900 mm (3 ft)
horizontally and 2.5 m (8 ft) vertically from
the top of the bathtub rim or shower stall
threshold. This zone is all encompassing and
includes the zone directly over the tub or
shower stall.
and it DOES not specifically exclude wall
sconces. If wet-listed fixtures are used, have I been wrong all these years?
Jim