shower/steam room

Status
Not open for further replies.
I have a person enclosing a large shower area (glass with glass door) all tile with a bench. They are having a steam generator installed. The ceilings are vaulted and go up to a skylight. They want recessed lights in this ceiling.
There will be a bench that will have an over head at about 6ft. They want recessed lights over this sitting area.
My questions will a typical recessed can and a shower trim meet the area (now that it has steam)? Are shower trims allowed to be installed in other then on a flat or horizontal ceiling? If I install a recessed light in this shower / steam room in an overhead at 6 ft do they have to be low voltage or on a GFCI?
And no I do not like the lighting plan.

Thanks
Mike
 

steelersman

Senior Member
Location
Lake Ridge, VA
redwood1957 said:
I have a person enclosing a large shower area (glass with glass door) all tile with a bench. They are having a steam generator installed. The ceilings are vaulted and go up to a skylight. They want recessed lights in this ceiling.
There will be a bench that will have an over head at about 6ft. They want recessed lights over this sitting area.
My questions will a typical recessed can and a shower trim meet the area (now that it has steam)? Are shower trims allowed to be installed in other then on a flat or horizontal ceiling? If I install a recessed light in this shower / steam room in an overhead at 6 ft do they have to be low voltage or on a GFCI?
And no I do not like the lighting plan.

Thanks
Mike
shouldn't be a problem having shower trims on a sloped ceiling and they shouldn't need to be gfi protected either.
 

dnem

Senior Member
Location
Ohio
NEC isn't going to require GFCI
UL isn't going to require GFCI unless you place a fan motor over the shower [or tub].
"typical recessed can and a shower trim" is fine as long as its rated for damp app [410.10(D)]. . Because of the steamer, you should look for a wet app rating.
 

dnem

Senior Member
Location
Ohio
DanZ said:
depending on the slope of the ceiling, you might want to make sure the cans you're installing can be sloped. I know lithonia has some that have sloped trim.

That's a good point. . It isn't even a shower question. . The can might not be rated to be installed in any slope anywhere in the house.
 
lighting steam room

lighting steam room

redwood1957 said:
I have a person enclosing a large shower area (glass with glass door) all tile with a bench. They are having a steam generator installed. The ceilings are vaulted and go up to a skylight. They want recessed lights in this ceiling.
There will be a bench that will have an over head at about 6ft. They want recessed lights over this sitting area.
My questions will a typical recessed can and a shower trim meet the area (now that it has steam)? Are shower trims allowed to be installed in other then on a flat or horizontal ceiling? If I install a recessed light in this shower / steam room in an overhead at 6 ft do they have to be low voltage or on a GFCI?
And no I do not like the lighting plan.

Thanks
Mike
Thanks all
 