donselec
Senior Member
- Location
- Aurora, CO, USA
I've studied 210 Part I. They're installing a shower steam unit and I have a 240-volt 30-amp single-phase circuit, residential. The steamer is 6K and pulls 25 amps. This slightly exceeds 80% of the 30A circuit rating of 24 amps. It is not a continuous load. There's nothing else on the circuit. The circuit uses a 30-amp breaker and #10 THWN copper wire. I can't see where this would be a problem or violation, does anyone have an opinion? Voltage drop should not be a factor. Thanks for any replies.