G & G Electric
I have question about a shunt circuit on an Ansul system, I'll try to keep it short and to the point. Circuit 28 is a shunt breaker, an individual circuit, feeding an oven. It goes through the NO contacts on a relay. That relay coil is held closed by circuit 29. 29 comes off of its breaker, hits a terminal block, and splits. One 29 goes through the NO Ansul system, and comes back to complete the shunt trip circuit when the handle near the oven is pulled. The other 29 goes from the terminal block and holds the relay closed. Also in that relay NO is the new kitchen RTU. My question is - When the handle is pulled and closes the dry contacts in the Ansul system, I know circuit 28 will open due to 29's circuit closing and energizing the shunt coil, but will circuit 29 open as well? I know, it sounds weird. It is a SqD shunt, and it has a sticker on it that leads me to believe the shunt circuit will trip when the shunt breaker trips. If this is correct, then when 29 opens, the RTU will shut down due to the relay being unenergized and returning to its open state. Or I could just run the line side of 28 to energize the coil, and I know then the RTU would shut down due to the shunt circuit 28 opening. Thanks ya'll!