It is essentially impossible to meet the requirements of SIL 3 with a single disconnecting means. To do so the device in question must have a Safe Failure Fraction of >99% (i.e. in this case, 99% of the failures of a shunt trip breaker would have to open)[IEC 62061 6.7.6.3].
I don't know of any SIL rated shunt trip breakers. The main reason is probably that shunt trip breakers unlike relays and contactors don't default to a safe state in the event of a loss of power to the control circuit. Think of it this way, if the wire to the shunt trip coil falls off you're screwed, you can't stop the machine; if the wire to a contactor coil falls off, you lose power and the machine comes to a stop, inconvenient but safe.