Here is the skinny.
Add a 120v dedicated ckt for shunt trip control wiring. The shunt doesn't draw much so a 15 amp will do.
The fire alarm contractor should supply a set of normally open contacts controlled by the fire alarm panel. Send 2 conductors from here to the shunt trip device. You have now put a single pole switch in line with the load ie the shut trip breaker.
Shunt tripping is only required when you have sprinklers in the pit, shaft, or control room and is triggered only by the heat detectors that are in proximity to the sprinkler heads that protect these areas. The heat detectors should be set to go off right before the sprinkler head and then shunt the elevator.
When smoke is detected in these areas the elevator will go into recall mode and return to the designated floor, open up and shut down.
Presumably, smoke will be detected before heat detectors and allow anyone on the elevator time through the recall function to exit the car before it has been shunted. And before a shower.
A couple other tips for elevators. Make sure that you have overcurrent protection in the control room and that your disconnect is in the right place. A good rule of thumb is no more then one step into the room. Make sure that it is lockable, and if there is an emergency let down system installed for the elevator; a set of contacts that is inter-locked to the disconnect is required.