shunt trip breakers

Status
Not open for further replies.

reskra

Member
Shunt trip breakers supplied with radiology equipment are tripping everytime the generator is tested in a hospital and have to be manually reset. Does anyone know what would cause this?
 

tallgirl

Senior Member
Location
Glendale, WI
Occupation
Controls Systems firmware engineer
reskra said:
Shunt trip breakers supplied with radiology equipment are tripping everytime the generator is tested in a hospital and have to be manually reset. Does anyone know what would cause this?

Where are the cables for the shunt trip part being routed? Do they hang out around anything that might not be energized when the generator is tested?
 

iwire

Moderator
Staff member
Location
Massachusetts
Assuming it is not the shunt causing it but the instantaneous trip unit that is casing this I would recommend changing the transfer switch programing to delayed transition.

What this does (if the ATS has the feature) is disconnect the load from one source then it waits for however long you program it for before reconnecting to the other source.

A quick transfer from one active source to another can cause breaker tripping. I believe the delay lets any supplied transformers or motors completely go dead before being energized again.

Any way adding a 1 second delay has worked for me in the past when customers had seeming random breaker tripping with transfer switch operation.
 

brian john

Senior Member
Location
Leesburg, VA
Or is this an undervoltage release..seen this more than once on ATS transfer....

Check the "shunt trip" (cause it may not be a shunt trip) for voltage when operating normally.
 