Member
Hi
In NEC, is there any requirement for a shunt trip coil for all kitchen equipment that produces heat from electricity?(I mean shunt trip coil for each equipment ckt)

Thanks n Regards

Siva
 
Re: Shunt trip coil requirement

I believe you are talking about electrical cooking equipment under a class 1 hood. Like in a restrant. This is not a NEC issue but it is a fire code issue. They want the power disconnected if the halon system goes off under the hood
 
Re: Shunt trip coil requirement

There have been many discussions of commercial kitchen "grease hoods" in this Forum.

NEC does not cover. NFPA 96 covers it. Read it closely.
 