Is a Shunt Trip for the controls circuit on a Natural Gas Water Heater required by code? If so, which code requires this? I can't find it anywhere. This is for a business type occupancy.
Thanks.
Is this in relation to a fire alarm panel?
No, unless the fire alarm code requires a shunt trip for a natural gas water heater.
Larger gas water heaters have controls to open the flue damper & open the gas valve & light the burners, simplified version of what goes on, but remove 120V power & it shuts down.
Don't confuse required E-stops needed on boiler systems with domestic water heaters. The rating of the boiler vessel is what kicks that requirement in. Domestic water heaters don't operate as as high of a temp or pressure. Shunt trip isn't a requirement on those either but is one possible method, you just need a method of removing power to burner controls from specified location(s).Is a Shunt Trip for the controls circuit on a Natural Gas Water Heater required by code? If so, which code requires this? I can't find it anywhere. This is for a business type occupancy.