Hi,
I have the following scenario:
Existing gear has a 600A breaker part of a kk interlock scheme for emergency whole building power. The 600A would not be adequate to provide for the entire facility but the generator is for a very specific set of loads to avoid losing process heat in a power outage and spoiling an entire batch of materials. The load is purely resistive so essentially we will be close to unity power factor. The generator they were able to get in a pinch is a 400kW/500kVA generator. Their loads only require half or less of that. The generator cannot be dialed back. The electrician wired everything in and the inspector then asked him to have an engineer look at it, here is what they did:
Gen with Integrated 800A CB --> Conductor --> 600A CB interlocked breaker in switchgear.
The issue is that they need this up and running yesterday, and everything these days has ridiculous lead times. The 800A CB in the generator has a shunt trip relay, I had a thought of a resolution, but not sure it is feasible. Seeing at the loads they intend to connect were previously behind a 225kVA gen without issue, and we have a list of possible load sources that could be connected at a single time (per 702.4(B), and 702.4(1)), is there anything that would specifically indicate that I could or could not use utility grade relaying with CTS on all 3 legs to manage provided current to not exceed 80% continuous of 600A (400kVA) / 100% non continuous (498kVA)? The only reference I see specifically to nameplate ratings are load related, not generator related, so my logic seems to tell me that if I am limiting full load current with a fail-safe device (if the device is inop the gen won't work). However, logic also tells me I am missing something . Another side note is that in all reality here the breaker is 100% rated and everything ahead of it is as well so we are talking 1A over at 80% power-factor highly improbable) that still causes the trouble; we are actually in the process of trying to figure out if everything is 100% rated while we work through solutions though don't know what that really does for us anyway.
In another time when breakers or generators weren't a 6 month + lead time, I would've just said do it right, but here they are really in a pinch, ever day could mean big $$$ lost if they have a power outage at the wrong time (which is not terribly uncommon).
Thanks in advance for your thoughts on this! Sorry if this seems like a whacky suggestion, open to other suggestions as well.
I have the following scenario:
Existing gear has a 600A breaker part of a kk interlock scheme for emergency whole building power. The 600A would not be adequate to provide for the entire facility but the generator is for a very specific set of loads to avoid losing process heat in a power outage and spoiling an entire batch of materials. The load is purely resistive so essentially we will be close to unity power factor. The generator they were able to get in a pinch is a 400kW/500kVA generator. Their loads only require half or less of that. The generator cannot be dialed back. The electrician wired everything in and the inspector then asked him to have an engineer look at it, here is what they did:
Gen with Integrated 800A CB --> Conductor --> 600A CB interlocked breaker in switchgear.
The issue is that they need this up and running yesterday, and everything these days has ridiculous lead times. The 800A CB in the generator has a shunt trip relay, I had a thought of a resolution, but not sure it is feasible. Seeing at the loads they intend to connect were previously behind a 225kVA gen without issue, and we have a list of possible load sources that could be connected at a single time (per 702.4(B), and 702.4(1)), is there anything that would specifically indicate that I could or could not use utility grade relaying with CTS on all 3 legs to manage provided current to not exceed 80% continuous of 600A (400kVA) / 100% non continuous (498kVA)? The only reference I see specifically to nameplate ratings are load related, not generator related, so my logic seems to tell me that if I am limiting full load current with a fail-safe device (if the device is inop the gen won't work). However, logic also tells me I am missing something . Another side note is that in all reality here the breaker is 100% rated and everything ahead of it is as well so we are talking 1A over at 80% power-factor highly improbable) that still causes the trouble; we are actually in the process of trying to figure out if everything is 100% rated while we work through solutions though don't know what that really does for us anyway.
In another time when breakers or generators weren't a 6 month + lead time, I would've just said do it right, but here they are really in a pinch, ever day could mean big $$$ lost if they have a power outage at the wrong time (which is not terribly uncommon).
Thanks in advance for your thoughts on this! Sorry if this seems like a whacky suggestion, open to other suggestions as well.