T takakimf Member Feb 8, 2006 #1 Would like to know whether it's best to shunt trip primary (13.8 kV) or secondary circuit breaker (2.4 kV) of building transformer under load?
Would like to know whether it's best to shunt trip primary (13.8 kV) or secondary circuit breaker (2.4 kV) of building transformer under load?
C charlie tuna Senior Member Location Florida Feb 9, 2006 #2 Re: Shunt trip i would say it is a matter of cost -- either shunt trip will be designed to handle the rated current flow. i would rather have it on the higher voltage breaker because it will be opening at a lower current..........
Re: Shunt trip i would say it is a matter of cost -- either shunt trip will be designed to handle the rated current flow. i would rather have it on the higher voltage breaker because it will be opening at a lower current..........
rick hart Senior Member Location Dallas Texas Feb 9, 2006 #3 Re: Shunt trip Since you probably already have relays on either, I would prefer a primary shunt trip. I assume the shunt trip is some sort of emergency power off?
Re: Shunt trip Since you probably already have relays on either, I would prefer a primary shunt trip. I assume the shunt trip is some sort of emergency power off?