Thanks, But the City I am in is requiring a shunt trip for all business and if under one roof a main trip for the whole building per NEC 2020 I cant find it
Code article your seeking is..
230.76 Manually or Power Operated
The service disconnecting means for ungrounded service conductors
shall consist of one of the following:
(1) A manually operable switch or circuit breaker equipped with a handle or other suitable operating means.
(2) A power-operated switch or circuit breaker, provided the switch or circuit breaker can be opened by hand in the event of power supply failure.
Obviously, the jurisdiction where you are working, having mandated option number (2)
As advised, check the local ordinance.