Ben Trueblood
Member
Could someone explain in the simplest form how a shunt trip circuit works?
Thanks
Thanks
I work with one AHJ that will not allow shunt trip breakers for under hood equipment shutdown.
kc8dxx said:I much prefer to use an Undervoltage Release mechanism instead of a Shunt Trip mechanism. That way if power is lost, the breaker trips. I am uncomfortable with not being able to trip the breaker because of a power loss, broken wire, open fuse, hungry rat, out of control forklift, etc etc.
steve66 said:I'm not sure you would want to do that with an elevator though. (Thats the most common application I see for shunt trip breakers.)
Steve
sceepe said:I work with one AHJ that will not allow shunt trip breakers for under hood equipment shutdown.
brian john said:What gives him the right to do this
dbuckley said:In my book, that inspector has made a good call. He may not have the "right", but long may he continue.
The shunt trip signal comes from the fire alarm master controller, however you can not tie this signal directly to the shunt trip device, since most shunt trip devices require more amperage to trip, than the shunt trip signal can deliver. The end result is you will burn out the shunt trip module within the fire alarm controller.Steve, I'm curious (I never worked on an elevator), how is a shunt trip used in an elevator circuit/control
davidr43229 said:The shunt trip signal comes from the fire alarm master controller, ..
The Shunt trip signal is sent only after a heat or smoke detectors hit a certain threshold and the elevator hits a home floor recall.So can I infur the fire alarm system shuts down the power to the elevators? Then someone has to reset them (shunt trip breakers) manually?
What if there are people actually using the elevator? Are there battery backups to power the elevator to the nearest floor? Are the people just stuck between floors? What if the fire fighters wanted to recall an elevator
davidr43229 said:Sorry it took me so long to reply.