Sumo
Member
- Location
- Salt Lake City, UT
- Occupation
- Electrical Engineer
I am installing a roll-up door operator in the compressor building of a natural gas pipeline. The area was deemed to be class 1 division 2. The building has hazardous gas detection which I will use to shunt trip the power feed from the control building if the gas level reaches 40% LEL.
2 questions:
1. Can I purchase a standard (non-rated) industrial roll-up door opener for this application?
2. Does the push button switch to operate the door opener (mounted inside the compressor building) need to be explosionproof?
My gut feel is that a non-rated piece of equipment may be installed in that environment (if shunt tripped) but that all conduit fittings and wiring methods must still meet class 1 div 2 requirements, including an explosionproof switch although there will be no power provide ignition to the explosive atmosphere (i.e. there is no provision in 501.115(B)(1) to allow non-rated switch when used in a shunt trip protection scenario).
What are your thoughts?
2 questions:
1. Can I purchase a standard (non-rated) industrial roll-up door opener for this application?
2. Does the push button switch to operate the door opener (mounted inside the compressor building) need to be explosionproof?
My gut feel is that a non-rated piece of equipment may be installed in that environment (if shunt tripped) but that all conduit fittings and wiring methods must still meet class 1 div 2 requirements, including an explosionproof switch although there will be no power provide ignition to the explosive atmosphere (i.e. there is no provision in 501.115(B)(1) to allow non-rated switch when used in a shunt trip protection scenario).
What are your thoughts?