Shunting a single 20a ckt.

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
If you need to do like what @LarryFine has posted, this contactor is the most economical way to do it. The contacts can be changed easily from N/O to N/C by which position you install the contact block in. Use the N/C position to turn on the fan, while using the N/O to turn the make up air off. (Series the make up air fan controls) Square D also makes a contactor that the contacts can be changed, but it’s more involved.
 

Attachments

  • IMG_1350.jpg
    IMG_1350.jpg
    44.4 KB · Views: 3
  • Like
Reactions: Jha

Jha

Member
Location
SC
Occupation
Electrician
It works, but probably not a great idea, the higher the available fault current the worse of an idea it may be. At very least how do you know you didn't destroy the light duty contact when you test it or it actually functions? May not work next time it is called on. You want low current to assure this doesn't happen.

An idea I never have done but have given some thought to is to use a GFCI breaker and create a neutral to ground fault with the control circuit.
Would you be using the control wires the same common and NC to the neutral screw on breaker and other control wire to the ground? I’m confused how that would possibly work?
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Would you be using the control wires the same common and NC to the neutral screw on breaker and other control wire to the ground? I’m confused how that would possibly work?
Creates an alternate path for the neutral current, so the breaker thinks there is a ground fault (actually, it is)
 

Jha

Member
Location
SC
Occupation
Electrician
Yes, in theory it works, but not designed for that type of application. Load neutral and N/O tie together on the load neutral screw.
And then common to ground? Seems odd cause when you put a meter between the two you get nothing
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
And then common to ground? Seems odd cause when you put a meter between the two you get nothing
When the contact closes, it parallels the load neutral, shunting some of the current, which in milliamp’s doesn’t take much. You can test the theory with a gfi receptacle, take the load neutral to ground, and it will trip.
 

kwired

Electron manager
Location
NE Nebraska
Class A GFCI's have a neutral to ground detection component. What it does is inject a signal that will travel through the output neutral through when faulted through the ground and back to the source then back to the GFCI via the ungrounded conductor. It will draw enough mA to trip the breaker on it's usual trip function.

Without that feature there needs to be enough load current so that the alternate path causes enough imbalance to cause the trip, so it won't work during a neutral to ground fault if there is no connected load at the time.
 