Side access concern, code violation?

nietzj

Senior Member
Location
St. Paul, Minnesota
Occupation
Electrician
I have an install of a new UPS. Facing from the front going left to right there are 2 battery cabinets, next the main breaker panel (MBP), last cabinet the UPS. All the clearances are fine. My only problem is in order to torque connections or service the MBP you potentially need side access which is blocked by the 2 battery cabinets. To move the battery cabinets conduit would need to be disassembled. If the side panel is removable is this a code violation?
 