I agree with you until the inspector (who is never wrongOriginally posted by charlie:
IMO, there is no requirement to ground aluminum siding.![]()
Dean,It would be up to the AHJ to determine if this was the case for your siding.
Is it possible the key word here is "likely"? The code doesn't appear to use the word possibly so maybe then the question is how is it likely? To me, likely means that the risk is high. How many buildings with aluminum or steel siding become energized, aside from possibly a lightning strike, in which case the grounding electrode conductor will probably not be adequate to handle the current anyway? I suppose it would be a judgement call by the AHJ?250.4(A)(4) requires electrically conductive materials likely to be energized to be connected to the electrical supply source to establish an effective ground-fault current path.
A voice of reason, thank you.Originally posted by don_resqcapt19:
How would you bond the siding system on a typical dwelling unit?
John,Originally posted by big john:
Iwire,
I'm assuming you also hooked the #6 to an EGC or something similar, yes/no? Are we talking about how to properly ground siding so that it will clear a fault, or are we talking about simply bonding it all together?
Thanks.
-John