RICK NAPIER
Senior Member
- Location
- New Jersey
I've been asked to send Siemens some information explaining why 3 spaces on neutral bars at main disconnect panels do not provide enough spaces for the standard dwelling installation in the hope they will expand to 5 spaces on their neutral bar. Normally you would have 2 neutrals, 1 ground and either a ground rod or concrete-encased electrode for 1 and metal piping as either an electrode or simply bonding as another 1 for a total of 5 connections. I have required electricians to install an additional bar per 250.24(4), or bonding 2 electrodes together and bringing the ground to an installed lug on the panel, or going from one electrode to the other then to the main panel again bringing the ground to an installed lug on the panel.
They have told me that they have only had this issue come up from some inspectors and contractors in New Jersey and think it may only be a local issue. I am hoping that this issue has come up in other locations and would like to hear from you so that I may pass this on to Siemens in hope of having them add 2 additional spots on their neutral bars. Thank you.
They have told me that they have only had this issue come up from some inspectors and contractors in New Jersey and think it may only be a local issue. I am hoping that this issue has come up in other locations and would like to hear from you so that I may pass this on to Siemens in hope of having them add 2 additional spots on their neutral bars. Thank you.