Danny89
Member
- Location
- Indian Land
For a 1/2 Hp motor pulling 4 amps single phase 277. with internal motor thermal protection. What size breaker should be used. Can NGB1B020 be used or does it have to be sized at 800 percent ...code reference T.430.52
I'm not sure if this breaker qualifies as instantaneous trip or inverse time breaker. I want to size the protection correctly for the the short circuit and ground fault protection. Motor it is supplying already has wired up internal overload protection. Any answers anyone?
I'm not sure if this breaker qualifies as instantaneous trip or inverse time breaker. I want to size the protection correctly for the the short circuit and ground fault protection. Motor it is supplying already has wired up internal overload protection. Any answers anyone?