Siemens QP series breakers

Status
Not open for further replies.

shawnfunk

New member
According to my research, Siemens QP series breakers does not allow multiple conductors.

I cannot find this information in black & white!

Can someone send reference or web site that clearly states single conductor only?!!

Thanks
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Re: Siemens QP series breakers

I am curious what "resaecrh" led you to beleive this if you have been unable to find it in black and white.

Wild guesses, rumor, and supposition from others who do not know either does not constitute research.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: Siemens QP series breakers

110.14(A) states that "Terminals for more than one conductor and terminals used to connect aluminum shall be so identified."

Be reverse logic, it can be safely assumed that terminals not identified as such are only suitable for one copper conductor.

Beyond that, try Google. :)
 