Siemens series rating chart says that the HQP breaker is series rated with class T (300V) as shown below.

I am wondering if this is saying I must strictly use a 300V class T fuse. What if I use a 600V class T fuse but my applied voltage is 208V? 208V is less than 300V. Would I still be able to achieve the series rating?

1727547854870.png
 
Siemens series rating chart says that the HQP breaker is series rated with class T (300V) as shown below.

I am wondering if this is saying I must strictly use a 300V class T fuse. What if I use a 600V class T fuse but my applied voltage is 208V? 208V is less than 300V. Would I still be able to achieve the series rating?
If the chart shows a 300V fuse, that is likely the one it was tested with.
The 600V fuse must have a slightly different performance and therefore is not interchangeable, which is why there are two different sections in the chart.
 
If the chart shows a 300V fuse, that is likely the one it was tested with.
The 600V fuse must have a slightly different performance and therefore is not interchangeable, which is why there are two different sections in the chart.
Got it.

What I am also wondering is why they didn't call out the bottom class T section as "(600V)"
 
Got it.

What I am also wondering is why they didn't call out the bottom class T section as "(600V)"
The bottom sections values probably apply to both 300V and 600V fuses.
Look at a QAF2, it can be series rated with a 1200A 600V or a 1600A 300V.
 
The bottom sections values probably apply to both 300V and 600V fuses.
Look at a QAF2, it can be series rated with a 1200A 600V or a 1600A 300V.
Weird though, if that was true then the HQS breaker would be on both top and bottom sections. How come HQS is only on the bottom section?
 
I was going through my old post because I think we talked about this a long time ago.

The post you made back in March you said they are for 600V only. What made you change your mind?

See below link post #7

https://forums.mikeholt.com/threads/understanding-series-rating-charts.2579598/
Without going back to my mindset at that time, I don't know. Maybe I didn't look at the chart at all, but it could have been because I didn't notice the limitation in the maximum fuse size at that time.
 