Does anyone know where I can find them? Or perhaps they dont have any? Only was able to pull up their two tier ratings on the web.
Maybe a stupid question, but wouldn't that just be the combination of 2 - two tier ratings?
Devices A,B, C from utility to branch. Say actual AFC is 65k. Say AFC at C is not significantly lower to allow its use without a series rating. AIC of A is 65k, B is 22K, C is 10k (full, not series ratings). Say a series rating exists for A and B, and also for B and C. Many will apply both to use these three devices together. The problem is, the AFC at B is not actually 22k so you cant use the B-C series rating. The only way to use these three together is if they have a tested three tier rating.
Square D seems to have a decent number of three tier ratings, Eaton as a few, but if I am reading that correctly, the first device has to be a fuse in all cases. Siemens I cant find any.