Siemens Two Pole AFCI Circuit Breaker

Status
Not open for further replies.
No, they are only listed for 240 volt use.

Do you have specs on the Siemens that I can look at? I called tech support a few years ago with Sq. D and they told me and sent information saying Sq. D would not work on 208 volts.
 
So what do all the apartments that are fed with 3 phases Y services do for afci protection

I did a remodel in a condo last year that had a majority of the circuits run as multiwire branch circuits. The panel in each unit was a single phase 208/120 volt single phase Sq. D panel. I called Sq. D tech support and they stated that the 2 pole Sq. D AFCI circuit breakers would not work on 208v. I'm curious if Siemens 2 pole AFCI circuit breakers are the same?
 
Is this a trick question? :? It's 208.
Yes so why did you say they were dp breakers. Someone can wire an apt with multiwire branch circuit and be stuck with needing dp breakers. I was surprised that if you wanted to add afci on an existing multiwire branch circuit that you could not do it in apts feed with 208V
 
Yes so why did you say they were dp breakers. Someone can wire an apt with multiwire branch circuit and be stuck with needing dp breakers. I was surprised that if you wanted to add afci on an existing multiwire branch circuit that you could not do it in apts feed with 208V

Because the double pole AFCI is limited to 120/240 volt circuits. We're arguing the same thing.
 
The only manufacturer that gives you a way out on a 120/208 panel that has MWBCs in it is G.E. and their Mod 3 breaker. You use two single pole breakers with their handle tie. Wire it to their spec, it is U. L. listed for that use.

Sent from my XT1254 using Tapatalk
 
Because the double pole AFCI is limited to 120/240 volt circuits. We're arguing the same thing.

I think Dennis' question is still unanswered though. If you're required to have AFCI breaker on a 2-pole circuit and the panel happens to be 208V, are you SOL if you didn't think to install a GE panel (per bsmith8691)?
 
I think Dennis' question is still unanswered though. If you're required to have AFCI breaker on a 2-pole circuit and the panel happens to be 208V, are you SOL if you didn't think to install a GE panel (per bsmith8691)?
If you are adding a new circuit you obviously would not use a multiwire branch circuit and if you are extending the circuit then use an afci Receptacle. Probably not a problem.

I guess knowing this is good info for planning
 
The only manufacturer that gives you a way out on a 120/208 panel that has MWBCs in it is G.E. and their Mod 3 breaker. You use two single pole breakers with their handle tie. Wire it to their spec, it is U. L. listed for that use.

Sent from my XT1254 using Tapatalk

But how do you connect the neutral of a MWBC?





Sent from my iPhone using Tapatalk
 