I have drive thru menu board sign attached sketch. There are 2 single pole 20 amp circuit breakers, under it is terminals and on top of the breakers are two receptacles isolated.
I have one branch circuit with one hot, one neutral, one EGC, one isolated EGC to the sign to power the menu board as well as the two receptacles.
The menu boards are considered their own structure they are outside on pad.
NEC 2014 section 600.6 requires operable switch or circuit breaker. Following questions:
1. Can the circuit breaker acts as the sign circuit breaker 600.6? It would be inside the back cover
2. Would the sign require grounding electrodes per NEC 2014 section 250.32?