jared albrecht
Member
- Location
- Anchorage
- Occupation
- Engineer
I have a service that consists of a ct enclosure and a feeder to an MDP with a 400 amp main breaker. the conductors from the ct enclosure to the MDP is one set of 500 MCM. the inspector is making me install signage on the service to annotate that no more than 380 amps can be connected to this service. this is due to the 500 MCM only rated for 380 amps. I am trying to determine the code that would derive the signage. Any ideas that would not require me to ask the inspector?