I'm trying to translate this section on Optional Standby generators:
702.8 Signs.
(A) Standby. A sign shall be placed at the service-entrance
equipment that indicates the type and location of on-site
optional standby power sources. A sign shall not be required
for individual unit equipment for standby illumination.
(B) Grounding. Where the grounded circuit conductor
connected to the optional standby power source is connected
to a grounding electrode conductor at a location
remote from the optional standby power source, there shall
be a sign at the grounding location that identifies all optional
standby power and normal sources connected at that
location.
"sign at the Grounding location" - does this mean this sign is at the generator or the service entrance?