Silly question...

Status
Not open for further replies.

emahler

Senior Member
we don't use much NM-B, but I know that they are coming out with all types of special cables (12-2-2, etc)....

here is the question, have they come out with a 12/2 romex with 2 grounds? and insulated and a bare in the same outer sheathing?

and would this be legal for the patient care area in a dentists office?

no, i haven't look it up...just thinking...thanks
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
no and no
517.13
(A) Wiring Methods. All branch circuits serving patient care areas shall be provided with an effective ground-fault current path by installation in a metal raceway system, or a cable having a metallic armor or sheath assembly. The metal raceway system, or metallic cable armor, or sheath assembly shall itself qualify as an equipment grounding conductor in accordance with 250.118.
 

360Youth

Senior Member
Location
Newport, NC
thanks...told you it was a silly question...

I have been on a CS Lewis kick lately, so here you go...

"Can a mortal ask questions which God finds unanswerable? Quite easily, I should think. All nonsense questions are unanswerable. "


All kidding aside, it is amazing how many different products I have learned of since perusing around here, so it is never a silly question to ask of such things.
 

nolabama

Senior Member
Location
new orleans la
dumber question wouldnt 12-2 with an inuslated and bare ground be 12-3 with one of the wires green instead of red - and if so wouldnt a roll of green tape fix that ?
 

mxslick

Senior Member
Location
SE Idaho
dumber question wouldnt 12-2 with an inuslated and bare ground be 12-3 with one of the wires green instead of red - and if so wouldnt a roll of green tape fix that ?

I think the 12-2-2 is actually 2 hots, two neutrals and a bare ground. :D

Brought about because of those PITA AFCI's.
 

nolabama

Senior Member
Location
new orleans la
You can't use 12/3 or 14/3 for two AFCId circuits. So 14-2-2 and 12-2-2 were developed.

i guess i dont follow - AFCI's are mostly only put in for inspection 'round here and promply pulled out - so you guys pull two homerun circuts on a 12-2-2 (its even refered to as 12/4 here) and j-box when you get where your going??
 