Silly semantics question, I know this does not matter but when doing load calcs for a 416Y/240 system, the transformer namplate says secondary is 416Y/240, however some of the breakers and receptacles use 415Y/240. What is the standard way to describe this system?
Going by simple math when we have 120 * SQRT(3) we get 207.87 and round up to 208V
likewise 277 * SQRT(3) = 479.77
so for a 240 to ground wye system 240 * SQRT(3) we get 415.69, so rounding up its 416V
We don't use 207V on receptacles and 208 on transformers.
So who's right ?
Example of 415V receptacle:
Example of 416V transformer
Going by simple math when we have 120 * SQRT(3) we get 207.87 and round up to 208V
likewise 277 * SQRT(3) = 479.77
so for a 240 to ground wye system 240 * SQRT(3) we get 415.69, so rounding up its 416V
We don't use 207V on receptacles and 208 on transformers.
So who's right ?
Example of 415V receptacle:
Locking Devices, Twist-Lock®, Insulgrip® Connector, 30A, 4 Pole, 5 Wire Grounding, 240/415 VAC, 3 Phase Y, NEMA L26-30R, Black and white Nylon | HBL2803 | Wiring Device - Kellems
Locking Devices, Twist-Lock®,Insulgrip® Connector, 30A, 4 Pole, 5 Wire Grounding, 240/415 VAC, 3 Phase Y, NEMA L26-30R, Black and white Nylon
www.hubbell.com
Example of 416V transformer