simple but dumb question

Status
Not open for further replies.

g-and-h_electric

Senior Member
Location
northern illinois
Occupation
supervising electrician
Mitsubishi ductless "mini split" installation....... Nameplate rating of 15 amp for compressor, .3 amp fan. They specify max OCP of 30, so a 25 would be fine. Based on the load any reason I cant feed it with #12? Article 440 ( I think) says I can. , but there is discussion with the HVAC guys saying it should be #10 . It is a short run of 25 feet or less, so voltage drop isnt an issue.

What do we all think


Howard
 

g-and-h_electric

Senior Member
Location
northern illinois
Occupation
supervising electrician
MCA on nameplate is 30..... I was interpreting 440 to say I can size conductors for load and mcp for reliable starting... BUT I have been wrong before....


howard
 