I believe the answer in my workbook is incorrect so I just wanted verification.
Question is:
what size service and service conductors for a multi family dwelling (paralleled in two raceways)?
load calculation comes out to 575 amps
answer sheet says 600 amp service which is correct but says the service conductors should be 350 kcmil at 310 amps. (2 conductors X 310=620 amps)
Shouldnt the service conductors be 300 kcmil rated at 285 amps because paralleled you get an equivalent of 570 amps which the next breaker size up is 600?
so couldn’t you use 300 kcmil conductors as opposed to 350 kcmil?