Just to double check there is not a problem with running 4 circuits (total 8 current carrying) #12 thhn through a 1/2” conduit to separate individual outlets. (All dedicated).
8 ccc reduces my ampacity to .70
#12 is at 90 degrees for derating and 30 amps
40X.7=21I
so in this case I should be able to pull 8 ccc and 1 equipment grounding conductor all within a 1/2” conduit if my calculations are correct?
thoughts?
8 ccc reduces my ampacity to .70
#12 is at 90 degrees for derating and 30 amps
40X.7=21I
so in this case I should be able to pull 8 ccc and 1 equipment grounding conductor all within a 1/2” conduit if my calculations are correct?
thoughts?