Simple code question

Status
Not open for further replies.
I just took the Experior Master electrical Exam and I have a question. One of the questions was, "How many risers (steps) are needed to require a 3-way switch at both ends?" (choices were 3-4-5-or 6) I spent alot of time looking this question up and still can't find it in the code book. I guess I am looking in all of the wrong places but I would love for someone to clear this up for me so I can sleep at night.
 

iwire

Moderator
Staff member
Location
Massachusetts
That is the section but it does not require the use of three ways.:wink:

You could use single poles on each landing, although the chances of having a happy customer would be slim.:D
 

allenwayne

Senior Member
Although the wording in that article doesn`t specify 3 way per say, It does allow one lighting outlet to supply lighting but it must have a switch at each landing to control that lighting outlet.How do you do that without a 3 way ?
 

allenwayne

Senior Member
Controlling one lighting outlet????? In order to control ONE the key word is ONE lighting outlet how do you propose to be able to CONTROL ( turn on and off) one lighting outlet with two single pole switches ???
 
Last edited:

allenwayne

Senior Member
Thinking about it the only way that it would work is if there was a two bulbed fixture that had two seperate switch legs at ONE lighting outlet and each switch leg controlled only ONE lamp holder.That wouldn`t be worth the trouble to do.

Although poorly worded I think the intent was for a 3 way.JMHO
 

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
Never under estmate the power of ingenuity...Think about the strings attached to porceliens and the stunts people do so that "the switch" can be pulled from by the entrance.
 
Well, now I don't feel so bad for not being able to find this answer. I have let it go because I am getting a headach trying to figure it out. Although, while looking answer this up I found in the 2005 INDEX under "SWITCHES" - "GENERAL USE" that it has art. 250.147 as one of the places to look, along with art. 404, & Def 100-I. I would like to know if anyone else's codebook is missing art. 250.147 or do I have an article thief in my house.
 
Ok, after my last post I looked up and actually read all of art. 210.70(2)(c). Moderator, you are good. For some reason, I looked over the last sentance time & time again. I actually answered "6 risers" on the test. At least I got one right. LOL.
 