Mustwin351
Senior Member
- Location
- Texas
210.8 lists location requirements for gfci protection and unless I missed it doesn’t specify class A. (I know it needs to be just trying to find the relevant section.) There is a mention in article 100 definitions but itonly an informational note.
422.5(A) clearly states class A.
Based on 2020 NEC.
I ask this as I have European equipment that the manufacture states needs residual fault current protection at 30 mA. There is a breaker made to that spec for my panel but it is very expensive.
422.5(A) clearly states class A.
Based on 2020 NEC.
I ask this as I have European equipment that the manufacture states needs residual fault current protection at 30 mA. There is a breaker made to that spec for my panel but it is very expensive.