Tom G
- Hartand Wisconsin
- Electrical worker
Good morning! Having a problem with simple math. I have 131 LED lights at .9 ma .9 multiply by 131= 117.9 amps seems high
Thank you! Iam in disbelief that 131 Led lights at 900ma total .1179 amps unless I have to move decimal pointYour multiplier it incorrect .9 milliamperes is .0009.
You changed the fixture current from 0.9 mA in your first post to 900 mA in your second post. Which is correct.Thank you! Iam in disbelief that 131 Led lights at 900ma total .1179 amps unless I have to move decimal point
Thank you the lights are going to be on a 277 volt circuitThe 900ma (0.9a) sounds more likely. And yes, well over 100 lights at almost an amp each will exceed 100 amps.
What type of fixtures are these? I haven't seen very many 250W LED fixtures.Thank you the lights are going to be on a 277 volt circuit