Hi there,
I am studying on my own and I am confused by motors.
See if this is right. Questions at bottom
5 hp. motor 240v. single phase integral thermal protection
table 430.248 28A FLC
430.22(A) 28x1.25 = 35A
table 310.16 75C column #10 THHN = 35A
short circuit protection (circuit breaker) 430.52(C)(1)
table 430.52 single phase
FLC 28x2.50 = 70A inverse time breaker
430.32(B) overload not required integral thermal protection otherwise use nameplate rating
430.102(B) disconnect required if motor in different location to circuit breaker
430.110 rating of disconnect 28x1.15 = 32A
430.109(F) horsepower rated cord and plug 5hp
SO...
1. Difference between a standard breaker and inverse breaker?
2.Which breaker protects ground fault or do you use fuses?
3.When do you use fuses?
Thanks
Jeff