Tables on maximum number of conductors in conduit. For example in table C1 it says the max number of #4 THHN in 1" conduit is 4. Does that mean you cannot also have at smaller EGC conductor in the conduit? I know if I do it the calculation way (adding up the areas of all the conductors) it says that I should be able to fit 4-#4 THHN and an #8 EGC in a 1" conduit. Is annex C enforcable code?
The reason I ask is I had a plans reviewer quote it and said that my conductors (on my plans) would not fit based on table C1 in annex C. And it was a similar situation (all conductor sizes have been changed to protect the innocent).
The reason I ask is I had a plans reviewer quote it and said that my conductors (on my plans) would not fit based on table C1 in annex C. And it was a similar situation (all conductor sizes have been changed to protect the innocent).