What size ground wire (equipment grounding conductor) is required for a 150 amp feeder?

Do I use the row for 100 amp (#8 EGC) , or the row for 200 amp (#6 EGC)? Is it sepcified anywhere in the NEC text?
 

cpinetree

Senior Member
Location
SW Florida
What size ground wire (equipment grounding conductor) is required for a 150 amp feeder?

Do I use the row for 100 amp (#8 EGC) , or the row for 200 amp (#6 EGC)? Is it sepcified anywhere in the NEC text?

Top right column heading - Not Exceeding (amperes)

150 exceeds 100 so you must use 200
 