I have a transformer feeding a service 80 ft of wire away. It feeds a 200 A meter ( 240/120 v 1 ph ) that feeds a 200 A 30 space 60 ckt home line load center/panel board. The 4/0 cu wire feeding feeding the meter calcs out to 12,000 AIC at the meter. If I install a simple 3r load center with a 22 k main breaker QOM2200VH and 10 K breakers ( HOM ) with a max of 60 A breaker, does the series rating of the main 200 A brkr protect the 10 k aic breakers ? The load center comes as a set with a few breakers, making it a very economical job.. ( outdoor load center Sq D HOM3060M200PRBVP ). For a slot store, though I may add a surge suppressor...
Thanx, dhsvcs
Thanx, dhsvcs