Sine wave

Status
Not open for further replies.
Re: Sine wave

Here's a three phase.

300px-Three_phase_voltages.png


It comes from this site.

Here's a single phase.

Sine_wave.png


And it comes from here.

I thought I'd be able to find some better material but it wasn't as easy as I expected. I'm sure there are some good animations out there somewhere. The animations I did find were a little too cheesey to bother with.
 
Re: Sine wave

If you measure line-to-line anywhere along the conductors (be they branch circuits or transmission lines), you cannot tell if the source is wired WYE or DELTA. The 3-phase graph that physis provided is representative of any set of 3-phase line-to-line voltages, or any set of line-to-neutral voltages from a 3-phase WYE source. But I?m not sure what a set of line-to-neutral voltages would look like for the configuration you have described.
 
Re: Sine wave

Stiff,

The three phases are always separated by 120 degrees whether you have a wye or delta, whether you are measuring phase voltages or line voltages.

The high leg 208V you mention would be at a different angle and lower amplitude, but this is not pure three phase.

I am confused by your reference to a neutral in a delta system. Do you mean the 120/240V neutral?

Rattus

[ June 25, 2005, 12:21 PM: Message edited by: rattus ]
 
Re: Sine wave

Originally posted by rattus:
Stiff,


I am confused by your reference to a neutral in a delta system. Do you mean the 120/240V neutral?

Rattus
LOL, I find that I have a difficult time communicating questions and ideas more and more. Sorry for the confusion, let me try again.

In a building that has a 120/240 three phase service with a high leg, I assumed the 208 (high leg) to neutral would have a higher amplitude than the two 120 legs. I also assumed the two 120 to neutral legs would be 180 degrees out from each other, not 120. This leads me to believe a sine wave graph of the two 120 volt legs would look like a single phase service, and I could not imagine what the 208 leg would look like in this graph.
 
Re: Sine wave

Stiff
You are correct in that a 240 delta would be 180 degrees out of phase with each other as referenced to the grounded (neutral). Draw a delta transformer and tap the ground. The ground is then 90 degrees out of either phase. 90 plus 90 equals 180, or it breaks the middle of 180 degrees.
This configuration there will be a point in time that both voltages will be zero at the same time.
 
Re: Sine wave

Stiff,

Let the diagram represent delta phase voltages as follows:

Va = 339Vpk*sin(wt + 0) or 240Vrms @ 0 deg.
Vb = 339Vpk*sin(wt + 120)or 240Vrms @ 120 deg.
Vc = 339Vpk*sin(wt + 240)or 240Vrms @ 240 deg.

Now let the "A" winding be center tapped.

The two 120V legs relative to neutral are:

V1 = 170Vpk*sin(wt + 0) or 120Vrms @ 0 deg.
V2 = 170Vpk*sin(wt + 180) or 120Vrms @ 180 deg.

The 208V leg is:

V3 = 294Vpk*sin(wt + 90) or 208Vrms @ 90 deg.

That is, V3 lags Va by 1/4 of a period, while Vb lags Va by 1/3 of a period.

Maybe Sam will draw us some more diagrams.

Rattus
 
Re: Sine wave

My sine wave capability is limited to a difficult to manage approximation. I think if I try to build a three phase sine wave the results would be below my acceptable quality standards.
Maybe I'll see what I can do later.

Edit: But I can't think of anything I'd put together that wouldn't look like the two at the top.

[ June 25, 2005, 05:43 PM: Message edited by: physis ]
 
Re: Sine wave

Here's some more useful stuff.

:(

I hate it when commerce uninvitedly interferes with intelligent thought.
 