Hi all, first post in the forum.
Probably this has been asked thousands of times, but I can't find an answer.
When calculating feeders for multifamily dwellings, is it correct to apply both methods from 220 Part IV, or are they mutually exclusive?
For example, using the image below: Is it correct to calculate the feeders that go from the Meter Enclosure to the 100A panels using 220.82 for each panel? (Assuming that they comply with the requirements of 220.82(A) ). That is, treat each 100A Panel as an individual dwelling unit.
After doing that, is it correct to calculate the Main feeder using 220.84? If not, what would be the proper method to calculate the Main feeder?
Probably this has been asked thousands of times, but I can't find an answer.
When calculating feeders for multifamily dwellings, is it correct to apply both methods from 220 Part IV, or are they mutually exclusive?
For example, using the image below: Is it correct to calculate the feeders that go from the Meter Enclosure to the 100A panels using 220.82 for each panel? (Assuming that they comply with the requirements of 220.82(A) ). That is, treat each 100A Panel as an individual dwelling unit.
After doing that, is it correct to calculate the Main feeder using 220.84? If not, what would be the proper method to calculate the Main feeder?