fusedneutral
Member
- Location
- Virginia, USA
- Occupation
- Engineering Consultant
Client has two buildings, 120/240 service (one 200A, one 400A), each with a separate meter, fed from the same on-premise pad pig, building grounds bonded at the main breaker service panels in each building. Client wants to put in a single 10K standby generator for emergency power in both buildings. 70ft between generator & each building. Control wiring for two transfer switches to one generator is a solved problem, no questions there.
If we use two pole transfer switches and connect all the neutrals together, that's parallel neutrals (generator neutrals in parallel with service neutrals). Not something we want to do.
If we use three pole transfers and a separately derived ground at the genny, then the ground wires between the genny and subpanels (also connected to the main breaker panels) become a parallel path to the service neutral because they are bonded to the service neutrals at the main panels. Really not something we want to do.
My initial thought is to use one two-pole transfer and one three pole transfer switch. This way all the neutrals are a single circut with hard connections (assuming they run to the same neutral bar on the pad pig), but the three pole transfer breaks the parallel neutral loop. The generator stays nonseparately derived, with ground conductor run to the two-pole building, no loops. So far so good. My question is about the fault current from the other building. In the building with the three pole transfer, the fault current path back to the genny (ground still bonded to the service panel) is now via the service neutrals, pad-pig buss bar, and panel/transfer in the other building to get to the genny.
Is this even reasonable? Are warning labels on the transfer switches & generator disconnect sufficient? Done many searches, but haven't found anything that quite scratches this itch.
If we use two pole transfer switches and connect all the neutrals together, that's parallel neutrals (generator neutrals in parallel with service neutrals). Not something we want to do.
If we use three pole transfers and a separately derived ground at the genny, then the ground wires between the genny and subpanels (also connected to the main breaker panels) become a parallel path to the service neutral because they are bonded to the service neutrals at the main panels. Really not something we want to do.
My initial thought is to use one two-pole transfer and one three pole transfer switch. This way all the neutrals are a single circut with hard connections (assuming they run to the same neutral bar on the pad pig), but the three pole transfer breaks the parallel neutral loop. The generator stays nonseparately derived, with ground conductor run to the two-pole building, no loops. So far so good. My question is about the fault current from the other building. In the building with the three pole transfer, the fault current path back to the genny (ground still bonded to the service panel) is now via the service neutrals, pad-pig buss bar, and panel/transfer in the other building to get to the genny.
Is this even reasonable? Are warning labels on the transfer switches & generator disconnect sufficient? Done many searches, but haven't found anything that quite scratches this itch.