Single Building - Multiple Elec. Services, Single Fire Alm Service

Status
Not open for further replies.
Looks ok to me, as long as the AHJ doesn't mind evacuating two buildings for every alarm. The rule that you have one F/A system per building isn't the same as one building per F/A system.
 
Looks ok to me, as long as the AHJ doesn't mind evacuating two buildings for every alarm. The rule that you have one F/A system per building isn't the same as one building per F/A system.
You shouldn't have to evacuate both "buildings". Even the most fundamental fire alarm systems today, usually have zone notification capability.
 
You shouldn't have to evacuate both "buildings". Even the most fundamental fire alarm systems today, usually have zone notification capability.
It depends on the size of the building(s). Beyond a certain population size (i don't know how big), it's actually more risky to have too many people fighting to get out at once.
 