Dear all,

I'm currently working in a project where the following design criteria are applied: "Low voltage cables shall be specified as single-conductors for cable sizes bigger to 1/0 AWG and multiconductors for cables smaller than 1/0 AWG". I have been looking in the NEC if there is any restriction to use multiconductors for sizes above 1/0 AWG and I can't find anything. I am aware that in some installations it might be easier to use "manageable" cable sizes to help in the routing process. However, I would like to know if (by standard or good engineering practices) there is something that recommends to use single-conductors from 1/0 AWG and on.

Thank you!
 
That sounds like a cable tray project and large multiconductor cables are used in tray. However the weight and stiffness can be an issue for long runs.
 
It seems to me the NEC recommendations is to run the multiconductor cables and single core cables in separate cable trays.

The 3 conductor-cable overall diameter is less than a triplex of single

core cables. However, in a cable tray, even following NEC Art 392[22 and 80] the ampacity will be less[14-20%].
 