Single conductor on cable tray

Status
Not open for further replies.

TMMB

Senior Member
Location
EGYPT
Occupation
Electrical Manager
My Q is :Can i use single conductors for lighting circuits (2.5mm2), socket circuits (4mm2) and A/C split circuits (6mm2) on metal cable tray or not as per NEC??
 
The smallest single conductor permitted in cable tray by the NEC is 1/0 and that is only in industrial occupancies.
 
it is the same concept in office building?

Yes. Look at Art 392.3 As Don stated, single conductors are only permitted in industrial establishments and then only for sizes 1/0 and larger and only then when they are listed and marked.
 