Single conductor use in CABLE TRAY

Status
Not open for further replies.

nmui

Member
Are there any single conductors, less than 1/0 size, that is rated for cable tray use? The code allows only single conductors sized 1/0 or bigger for use at 120V, so other than the exceptions listed, when can 120V single conductor be used for cable tray?
 

russ

Senior Member
Location
Burbank IL
Re: Single conductor use in CABLE TRAY

392.2(B)(1) seems to say it all. You can't use anything under 1/0, except for the grounds
 

nmui

Member
Re: Single conductor use in CABLE TRAY

Does anyone know why the NEC does not allow for single conductors to be installed in the cable tray below 1/0?

Thanks
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Single conductor use in CABLE TRAY

You need to find the Technical Committee Report and Technical Committee Documentation (these documents are now called Report on Proposals and Report on Comments) for the 1968 code to find out the reason. Prior to the 68 code smaller single conductors were permitted in cable tray. My code documentation starts with the 84 code so I can't tell you the reason.
Don
 