Single conduit or parallel

mannyb

Senior Member
Location
Florida
Occupation
Electrician
320 meter with parallel service feeds . We are installing ATS for new generator and limited space. I can only fit 1-3" conduit at bottom of meter can over to new ATS. Is it wise to install 1 conduit or 2 for parallel conductors to ATS
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What distance? 24" or less no derating so a single conduit would be easier without have to change the condcutor size.
 
I would probably just install one for something like that. Unless you have a load calc that is close to 400, I would probably just use two sets of 4/0 AL which would be 328 amps which is plenty 99.976% of the time. 2.5" would be fine for that.
 

mannyb

Senior Member
Location
Florida
Occupation
Electrician
I would probably just install one for something like that. Unless you have a load calc that is close to 400, I would probably just use two sets of 4/0 AL which would be 328 amps which is plenty 99.976% of the time. 2.5" would be fine for that.

Parallel conductors in same conduit?
 