NEC 392.10(B)(1)(a) indicate the single conductors smaller 1/0 AWG are not allowed for use on cable trays in industrial establishments. Article 392.22(B)(1)(d) doesn't recognize any conductors less than 1/0. I have a feeder run that consists 4#3/0 & 1#3Gn (single conductors) that will be installed on cable tray. My question is: does the limitation of using minimum size conductor (#1/0) is also includes the equipment ground conductor? in another word, do I have to change the #3G conductor to 1/0 or there is an exception for equipment ground conductors that we can use smaller size than 1/0?